Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Can I control the indoor temperature without latent energy demands?

asked 2016-03-12 11:35:04 -0600

h.silva's avatar

I am running a model with ideal air loads controlling only the temperature setpoints, but I was getting latent cooling loads even though I have not set any humidity limits.

I need to define a temperature range and check its effect on the energy consumption and in the relative humidity, but without affecting the humidity ratio. Is this possible?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2016-03-14 10:13:32 -0600

Adam Hilton's avatar

I don't think this is possible in the OS gui but you can set the SHR to 1 for the ideal air loads system either by using a measure or in energy plus and this should prevent any moisture from being removed.