Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Creating the geometry for plenum in Openstudio

asked 2016-03-10 11:40:40 -0600

updated 2018-07-07 10:36:56 -0600

I have watched This video that demonstrates how to create the geometry for and then hook up supply and return air plenums. And my question is that in practice plenums spaces are separated like construction A in the figure below and why in this video plenums are like construction B? I prefer the video approach but I hope it does not have significant effect on the result.image description

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
7

answered 2016-03-10 12:47:58 -0600

updated 2016-03-10 12:49:24 -0600

Some practical considerations, depending on your next modeling steps:

  1. Case A1: you model individual plenum spaces as in case A and then create zones for each space. The model will have more zones, which might make your workflow cumbersome, as you will have to work around all these other zones while inputting HVAC equipment, etc., and apply each plenum zone as a return air plenum for the corresponding conditioned zone in an air loop (if you are intent to use them that way). However, you might see an advantage in simulation time, since although you have more zones, each zone will have fewer surfaces, which improves the zone air heat balance calculation time. Additionally, the simulation will be able to capture more granularity with the plenum temperatures (e.g. perimeter plenums have higher/lower temperatures than core plenums) which could effect space temperature/HVAC interaction, as well as any specific loads transferred from the conditioned space to the plenum (like heat from lights that go to the plenum).
  2. Case A2: you model individual plenum spaces as in case A but assign all plenum spaces (say, by floor) to a single thermal zone. This would make working in your model easier, since you have fewer total zones to work with in the model. You would possibly see longer simulation times, though, as the plenum zone has more surfaces and internal mass objects (matched surfaces between spaces that are both part of the same zone get translated into EnergyPlus internal mass objects) that require calculations for the air heat balance. Heat conduction between the plenum and the conditioned zones will also be affected, since your plenum space is now a single air volume, without any perimeter/core variation.
  3. Case B: functionally most similar to A2 above, except you will not have as many internal mass objects in the plenum zone, since there aren't matched 'interior' surfaces.

The method that works best for you will depend on what effects you are most concerned about in your simulation, balanced with the effort and time to set up and simulate them. I find that case B is usually fine, but admittedly have not done a comprehensive analysis of how plenum modeling effects the overall results.

edit flag offensive delete link more

Comments

@Enric ,Thank you for your helpful info.

4Designer's avatar 4Designer  ( 2016-03-12 04:19:50 -0600 )edit
4

answered 2016-03-10 12:05:33 -0600

I'm coming for the viewpoint of the OpenStudio software capabilities more than the practical considerations. I think the intent of the video is simply to demonstrate that you can match plenums to multiple zones if you need to. This is not a requirement and you can certainly also match plenums one to one with zones in OpenStudio like you are showing in A.

Other practitioners are better suited to answer what is most realistic to see in practice.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-03-10 11:40:40 -0600

Seen: 874 times

Last updated: Mar 10 '16