Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Surface Inside Face Solar Radiation Heat Gain Rate vs SurfaceProperty:SolarIncidentInside

asked 2016-03-02 15:47:24 -0600

updated 2016-03-02 16:48:37 -0600

Dear Everyone,

I am trying to simulate extremely complex environments using EnergyPlus and Radiance. Since I am used to use Radiance, my apporach is to

  1. Calculate Solar irradiance over walls
  2. Create a Schedule for EnergyPlus that will be read using the SurfaceProperty:SolarIncidentInside.

However, I am having some trouble reading the documentation. Even though its name is SolarIncidentInside, then the documentation basically says the schedule will replace the absorbed solar radiation... the units are W/m2. All cool for now.

However, when I try to report it using the Output:Variable,*,Surface Inside Face Solar Radiation Heat Gain Rate per Area,hourly;, I do not get the same value as in the Schedule... and they do not even match the values multiplied by the surface absorbtance.

Can anyone please explain this discrepancy to me?

Kind regards,

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2016-03-03 03:03:57 -0600

Chandan Sharma's avatar

From the source code (SolarShading.cc, line 6758)

AbsIntSurf = Construct( Surface( SurfNum ).Construction ).InsideAbsorpSolar;
//SolarIntoZone = GetCurrentScheduleValue(SurfIncSolSSG(iSSG)%SchedPtr) * Surface(SurfNum)%Area
SolarIntoZone = GetCurrentScheduleValue( SurfIncSolSSG( iSSG ).SchedPtr );
AISurf( SurfNum ) = SolarIntoZone * AbsIntSurf;

Schedule value gets multiplied by the solar absorptance of the inside material of the construction. If the solar absorptance of the inside material is set to 1, as shown below, it should fix the above issue.

  Construction,
    Room Ceiling,            !- Name
    Plywood - 3/8 in,        !- Outside Layer
    2x6 Wood Stud R19,       !- Layer 2
    Gypsum board - 5/8 in;   !- Layer 3

  Material,
    Gypsum board - 5/8 in,   !- Name
    Smooth,                  !- Roughness
    0.015875,                !- Thickness {m}
    0.17,                    !- Conductivity {W/m-K}
    800,                     !- Density {kg/m3}
    1090,                    !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    1.0,                     !- Solar Absorptance
    0.3;                     !- Visible Absorptance
edit flag offensive delete link more

Comments

Thanks very much, Chandan. That was very very helpful.... The reported values and the schedule still do not match, though.

I read somewhere that the scheduled values are used to "propagate" Radiation within the room. Is that so? That is... Solar radiation arrives to the surfaces, and then EnergyPlus calculates the solar radiation that would end up in all other surfaces due to intereflections.

gmolina's avatar gmolina  ( 2016-03-03 06:04:23 -0600 )edit
1

If that doesn't fix the issue, the only other thing can recommend is to report Surface Inside Face Lights Radiation Heat Gain Rate per Area and see if it has non-zero values. That would probably explain the difference. I never had to use this object. Hopefully others can shed some more light into it.

Chandan Sharma's avatar Chandan Sharma  ( 2016-03-03 19:56:49 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2016-03-02 15:47:24 -0600

Seen: 497 times

Last updated: Mar 03 '16