How to set minimum fan flow rate for VFD?

asked 2016-02-22 12:31:23 -0600

NickC's avatar

updated 2016-07-13 10:21:36 -0600

In practice, it is common for AHU VFD fans to have some set minimum motor frequency. I've been trying to implement this is an OS/E+ model but seem to be stuck (i.e. you need to fix the fan so it never goes below 30 Hz)

@Kyle Benne seems to be asking about this as well...but not sure if he ever got any satisfaction. https://unmethours.com/question/11631...

Anyone know how to accomplish this?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2016-07-13 11:58:57 -0600

I think you could use Fan:ComponentModel for that. The field Motor Maximum Speed seems pretty aligned with what you do.

The drawback is that the object seems pretty detailed (or overkilled, depending on who's asking), and you'd have to implement it in an EnergyPlus measure if you want to stay within the OpenStudio ecosystem.

edit flag offensive delete link more

Comments

@Julien Marrec Thanks for the advice! Minimum motor freq. is an important feature and hopefully will make it into OS in future releases. For now, E+ it is :)

NickC's avatar NickC  ( 2016-10-28 22:23:01 -0600 )edit