Cannot enable CO2 concentration calculation in OpenStudio

asked 2016-02-17 15:59:37 -0600

I tried to enable CO2 concentration calculation in OpenStudio by the following setting

image description

In which the "CO2_ConcentrationSchedule" is a schedule with value 400 ppm.

However in the generated IDF file, I did not see the "ZoneAirContaminantBalance" object. Which I suppose I should see the following object:

image description

edit retag flag offensive close merge delete

Comments

what type of schedule did you use for the co2 concentration?

poppo92's avatar poppo92  ( 2016-11-29 08:43:16 -0600 )edit

I was just using a constant schedule of 400 ppm for the outdoor CO2 concentration.

TiejunWu's avatar TiejunWu  ( 2016-11-29 09:02:16 -0600 )edit

I'm not able to see it. I'm in "Schedules" in OS, and if I want to create a new one, these are the possibilities: dimensionless, fractional, activitylevel, OnOff, capacity, clothing, controlmode, delta temp, mass flow rate, power density, percent, pressure, rotation per minute, velocity, temperature, volumetric flow rate. Which is the correct one?

poppo92's avatar poppo92  ( 2016-11-29 09:35:57 -0600 )edit
2

I used a program based on OpenStudio SDK to generate the model.

For your case, even though the schedule type options in OS does not show a "CO2 Centration" type, you can use any schedule type that is continuous and does not have a upper limit, set the schedule value to 400 should work fine. The real issue with the OpenStudio User Interface is that you cannot assign the created schedule to the "Outdoor Carbon Dioxide Schedule Name" input box in the "Zone Air Contaminant Balance", which is under the "Simulation Settings" tab, it does not work even if you type in the schedule name.

TiejunWu's avatar TiejunWu  ( 2016-11-29 10:11:11 -0600 )edit

So, I know "thou shalt not edit the .osm file", but for grins, I noticed that each "OS:Controller:OutdoorAir" object also has a "!- Controller Mechanical Ventilation" line, and that in turn links to a "OS:Controller:MechanicalVentilation" object. In it, one can edit the "!- Demand Controlled Ventilation" line to say "Yes", rather than "No" or be empty. I believe the "HVAC->Ventilation->Enable Demand Controlled Ventilation OpenStudio" measure does the same thing.

Matt Koch's avatar Matt Koch  ( 2017-08-07 17:52:51 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2016-03-01 13:25:30 -0600

This appears to be a bug. I have reported it here.

edit flag offensive delete link more

Comments

Moved this issue here

macumber's avatar macumber  ( 2016-03-01 13:36:55 -0600 )edit

Just wondering if this is resolved? I'm trying to figure it out based on the thread you've attached but I'm not really sure

m.habib's avatar m.habib  ( 2020-06-29 09:09:36 -0600 )edit

I can confirm this issue has been resolved.

TiejunWu's avatar TiejunWu  ( 2020-06-29 09:29:43 -0600 )edit

Unfortunately it still doesn't seem to be working on mine. I'm using Open studio 2.9.1 so possibly it is an outdated version

m.habib's avatar m.habib  ( 2020-06-30 07:27:21 -0600 )edit