Setpoint Manager Outdoor Air Reset [closed]

asked 2016-02-04 10:12:44 -0500

Dustin's avatar

updated 2016-02-04 10:38:14 -0500

Hello all,

I am wondering if there is setpoint manager similar to the SetpointManager:OutdoorAirReset that can be used to vary a water temperature based on the outdoor air temperature?

Thanks

edit retag flag offensive reopen merge delete

Closed for the following reason the question is answered, right answer was accepted by Dustin
close date 2016-02-04 10:44:45.421601

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-02-04 10:25:24 -0500

updated 2016-02-04 10:28:07 -0500

How about SetpointManager:OutdoorAirReset :) ?

It works on plant loop just fine too. The documentation is pretty confusing on this since it mentions Supply Air temperature, but a plant loop will gladly accept it too. In fact, for many of the water reset (Hot water or chilled water) in ASHRAE Appendix G, this is what you need to use.

edit flag offensive delete link more

Comments

I've found the related question I was thinking about: here

Julien Marrec's avatar Julien Marrec  ( 2016-02-04 10:29:24 -0500 )edit

Thanks Julien that was confusing me where it said Supply Air temperature. I appreciate the quick response.

Dustin's avatar Dustin  ( 2016-02-04 10:44:40 -0500 )edit