Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

What is the Cooling Sizing Parameters - Zone Cooling DesignSupply Air Temperature for?

asked 2016-02-03 20:20:30 -0500

VictoriaEagen's avatar

updated 2016-02-03 23:06:29 -0500

What is the Cooling Sizing Parameters - Zone Cooling DesignSupply Air Temperature for?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2016-02-03 21:00:30 -0500

That parameter is used in the zone sizing calculation to determine the volume of air required to cool the zone to the zone thermostat setpoint temperature at design conditions. If you use any sort of auto-sizing capability in your simulation, this is a very good chapter of the documentation to familiarize yourself with.

edit flag offensive delete link more

Comments

So it is kind of like what you would want the air temperature to be supplied at to over compensate for the load? Is this a calculation I need to do?

VictoriaEagen's avatar VictoriaEagen  ( 2016-02-03 23:16:27 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-02-03 20:20:30 -0500

Seen: 342 times

Last updated: Feb 03 '16