Coil sizing check in E+
Hello, i would like to manually verify DX coil sizing in zonal equipment. The zone coil load should include ventilation and infiltration latent load. But unfortunately E+ standard report doesn't have them in desired format (g/kg instead of W). Update from Mr. Rraustad suggestion and E+ documentation : input as follow : Bases on psychrometric coil sizing formula :
set standard air density (1,2 kg/ m3)
mixed air flow = User Calc air flow =0.884 m3/s = 0.857(return air flow) +0.027 (outdoor air flow)
Enthalpy outdoor (36oC, 0.02207g/kg) = 92.87 kJ/kg ;Enthalpy return air/room air (26oC, 0.01138 g/kg) = 55.21 kJ/kg
Enthalpy supply air (14oC, 0.009 g/kg) = 36.87 kJ/kg
Enthalpy mix = ( Outdoor air enthalpy * Outdoor air flow + Return air flow * Return outdoor enthalpy)/mixed air flow = 56.37 kJ/kg -> air temperature = 26.3 oC air density = 1.157 kg/m3
Performance CAPFT : x = mixed air wetbulb = 19.68 oC , y = outdoor drybulb = 36 oC
CapFT= 1.5509 + (-0.07505) * 19.68 + 0.0031 * 19.68^2 + 0.0024 * 36 + (0.00005) * 36^2 + 36 * 19.68 *(-0.00043) = 1.121
Coil capacity = (Enthalpy mix - Enthalpy sizing zone ) * (air density) * (airflow) / (CapFT)
= (55.21 - 36.87) * 1.157 * 0.884 /1.121 = 17782 W
The coil report for PTAC :
Great Thanks to Mr Rraustad for validation.
Which E+ reports are you looking at?
i look at component sizing summary and equipment summary reports. i focus on basic sizing calculations of local system like PTHP, PTAC, VAV box,...
I stepped through the PTHP example file last night and found a match to the DX cooling coil size. I'll have to repeat that tonight. Or if you send me your file, I'll validate your coil.
Please check here IDF link i made thermal zone 101 sizing different with other .
Your file: Mixed T = 26.27, w = 0.01171, WB = 19.71, H = 56.248, rho = 1.1566, flow = 0.8838 CapFT = 1.12193, SupplyH = 36.81, Q = (56248-36810) * 1.1566 * 0.8838 / 1.12193 = 17710.2 W compared to 17712.08 W (rounding)