PV panels not working properly
I have two E+ models that are identical except for the PV generator capacity. I have defined the PV array as:
- PhotovoltaicPerformance:Simple (90% surface fraction, 15% fixed efficiency)
- Generator:Photovoltaic (decoupled, 1 series string, 1 module)
- ElectricLoadCenter: Distribution (Baseload, 0W purchased electric demand limit)
- ElectricLoadCenter:Inverter:Simple (on 24/7, .3 radiative, .9 efficiency)
- ElectricLoadCenter:Generators (1w for one model, 50,000w for the other model)
The results are almost identical, which makes no sense to me.
I reported Photovoltaic:ElectricityProduced J for both Northern hemisphere models and see:
- almost identical values in both models
- hourly values are non-zero when the sun is gone (as they should be)
- uniformly low values in both models (January is never greater than ~5,000w, July is never greater than ~8,000w)
I might be talked into believing the low values, but can't imagine or figure out why both models, which have vastly differing power output, show identical results. Help, please!
Have you looked at the ElectricLoadCenter:Distribution output for Total Electric Energy Produced? The report for the Photovoltaic may be the DC potential of the panels.
Is it possible to make a link to your model? It sounds like there may be an availability schedule limiting the PV generation time. Also, shouldn't there be zero PV electricity produced when the sun is gone? You say "hourly values are non-zero values when the sun is gone (as they should be)".