why vrf system by autosizing in equest generate many unmet hours
Can someone help me?, I modeled a PVVT system with variable speed compressor to represent a VRF system in eQuest, but the BEPU report show to many unmet hours (2400 app between cooling and heating). This is weird, to being an autosizing system, should not comply with the requirements "automatically" or to least not generate so many unmet hours? I think it's because some equipment supply thermal energy two to three zones and the flow of does not reach. To analize this condition I simulated a chiller with fancoils units in autosizing, and the unmet hours are 800 app.
Do you have zonal exhaust? Or is one of your zone adjacent to a semi-heated or unconditioned space?
Julien, the model do not have a exhaust system, neither zones adjacent to semi-heated or unconditioned space.
There are a couple things which come to mind. The first is related to Julien's point above - while the BEPU report gives the coincident unmet hours for the building [which is what LEED/Apdx G care about], use the SS-R report to check which zone[s] have the unmet hours. This will narrow it down. Secondly, you mentioned that some equipment serves multiple zones, for PVVT a control zone must be specified. Two parts 1-is this in the "worst" zone? 2-does it match plans? PVVT will control to the needs of the Control Zone, other zones get what they get.
The final thing, with auto-sizing, from the DOE2 documentation I've seen, the calculations use the Design Day data, which does not necessarily align / can be different from the weather file. Check that the Design Day inputs make sense [schedules/setpoints/etc]
@rraustad, how does one move a comment to become an answer?