Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Plant Operation Schemes in EnergyPlus example files

asked 2015-12-23 18:43:52 -0500

Chandan Sharma's avatar

Several EnergyPlus example files (e.g. CoolingTower.idf, ElectricEIRChiller.idf, CentralChillerHeaterSystem_Cooling_Heating.idf etc. to name a few) have two cooling load range based plant operation schemes specified for on peak and off peak operation. But same operation scheme name ("Peak Operation") was specified for both on peak and off peak periods. Some of these files which do have "Off Peak Operation" cooling load based operations scheme, they refer to same plant equipment list which is associated with "Peak Operation" scheme. This seems counter intuitive as this means that same plant equipment is always running to meet the cooling loads regardless of peak/off peak period and that second cooling load based scheme is actually redundant.. Is this as designed? Another question on UnmetHours led to this current question.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2016-01-12 10:39:50 -0500

This is a known issue that has propagated across many example files. For each one, it should be fixed to use an appropriate equipment list, or the dual schedules should be removed. https://github.com/NREL/EnergyPlus/is...

edit flag offensive delete link more

Comments

Thank you Mike.

Chandan Sharma's avatar Chandan Sharma  ( 2016-01-12 21:51:13 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2015-12-23 18:43:52 -0500

Seen: 293 times

Last updated: Jan 12 '16