Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

What object should I put to simulate a only sensible heat - heat recovery.

asked 2015-12-14 08:16:42 -0500

J Monteiro's avatar

updated 2015-12-14 08:18:23 -0500

Hi,

I want to know what´s the object that I've to use to model a only sensible heat recovery? I found in openstudio a sensible and latent heat recovery, but in my case I don't have latent heat recovery. Should I put the values of latent effectiveness to 0%?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
2

answered 2015-12-14 08:56:11 -0500

Yes. This is noted in the I/O Reference description of the Latent Effectiveness fields for HeatExchanger:AirToAir:SensibleAndLatent: "Specify this value as 0.0 if the heat exchanger does not transfer latent energy."

edit flag offensive delete link more

Comments

Thanks I understand now

J Monteiro's avatar J Monteiro  ( 2015-12-14 09:20:42 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2015-12-14 08:16:42 -0500

Seen: 176 times

Last updated: Dec 14 '15