Ground temperature warning in the simulation of EnergyPlus

asked 9 years ago

tech91's avatar

updated 9 years ago

How can I solve this problem in EnergyPlus when I do the simulation?

Program Version,EnergyPlus, Version 8.4.0-832e4bb9cb, YMD=2015.12.02 09:25,IDD_Version 8.4.0
   ** Warning ** GetHTSurfaceData: Surfaces with interface to Ground found but no "Ground Temperatures" were input.
   **   ~~~   ** Found first in surface=A84D86
   **   ~~~   ** Defaults, constant throughout the year of (18.0) will be used.
Preview: (hide)

1 Answer

Sort by » oldest newest most voted
7

answered 9 years ago

The warning is pretty clear: you have surfaces in contact with ground, but you haven't specified ground temperatures in your model.

If you don't want to see this warning, you need to put some ground temperatures. Check out the Input/Output reference, starting at Site:GroundTemperature:BuildingSurface.

As stated:

Caution: The “undisturbed” ground temperatures calculated by the weather converter should not be used in building losses but are appropriate to be used in the Site:GroundTemperature:Shallow and Site:GroundTemperature:Deep objects. The reasoning (for building losses) is that these values are too extreme for the soil under a conditioned building. For best results, use the Slab or Basement program described in this document to calculate custom monthly average ground temperatures (see the Ground Heat Transfer section). This is especially important for residential applications and very small buildings. If one of these ground temperature preprocessors is not used, for typical commercial buildings in the USA, a reasonable default value is 2C less than the average indoor space temperature.

Documentation on how to use the Detailed Ground Heat transfer with the preprocessors Slab or Basement is here.

There's also the option of using @Neal Kruis's Kiva

Preview: (hide)
link

Comments

Thanks for the support. Could you explain better temperatures assigned to the ground of a office building (thermal zone)? Amsterdam location. There is a table of the average monthly temperatures?

Thank you so much

tech91's avatar tech91  ( 9 years ago )

If you want to have accurate temperature, you need to use a preprocessor (slab, basement, or kiva) and calculate them based on your actual constructions in contact with the ground and the weather file for your location. If you want to know how to do that, post another question and I'm sure some experts will help you (I'm definitely not one of them).

Otherwise, as stated in the I/O reference guide bit that I posted above, you can put 2C below your indoor temperature.

Julien Marrec's avatar Julien Marrec  ( 9 years ago )
1

More info here

Jamie Bull's avatar Jamie Bull  ( 9 years ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 9 years ago

Seen: 1,789 times

Last updated: Dec 02 '15