asked 2015-11-01 11:41:12 -0500

s_pourm's avatar

updated 2015-11-01 15:10:19 -0500

Hi

I defined the outside face convection coefficient as an output. I see in some hours during the simulation, this coefficient is 1000 !!! How is that possible? And also in general , which method is more accurate? Because I changed the SurfaceConvectionAlgorithm:Outside from DOE-2 to AdaptiveConvectionAlgorithm and saw a significant difference in one of my outputs.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2015-11-01 14:14:21 -0500

According to Energyplus Engineering Reference (http://bigladdersoftware.com/epx/docs...):

Note that when the outside environment indicates that it is raining, the exterior surfaces (exposed to wind) are assumed to be wet. The convection coefficient is set to a very high number (1000) and the outside temperature used for the surface will be the wet-bulb temperature. (If you choose to report this variable, you will see 1000 as its value.)

It seems that you have rain data included in your weather file.

edit flag offensive delete link more

Comments

Thank you. Thats right.

s_pourm's avatar s_pourm  ( 2015-11-01 20:00:28 -0500 )edit