I've modeled my baseline with the appropriate oversizing ratios for heating and cooling (1.25 and 1.15, respectively). Do I keep this oversizing in my proposed model?

asked 2015-10-29 11:54:45 -0600

new2modeling's avatar

updated 2017-05-08 15:47:02 -0600

I am using eQUEST. The model is for office spaces that have yet to find tenants. The proposed model is based on the minimum requirements of the lease for tenant fit-outs. In this case, tenants are required to have equipment with a minimum SEER value of 15. I can model this just fine, but do I need to keep the oversizing that I had in the baseline (since there is no specified equipment and therefore no specified capacities)?

Thanks,

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2015-10-29 12:50:56 -0600

My understanding is that where components of the Proposed design are not specified or designed, these components should meet the requirements of the Baseline building. In this case, that would mean that the sizing factors in the Proposed should match the sizing factors in the Reference. See ASHRAE 90.1-2007, Table G3.1.10 (Proposed) HVAC Systems. "Where no heating/cooling system exists or no heating/cooling system has been specified ... System characteristics shall be identical to the system modeled in the baseline building".

edit flag offensive delete link more

Comments

I suspected as much, thanks for confirming.

new2modeling's avatar new2modeling  ( 2015-10-29 13:51:06 -0600 )edit