Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

How can I connect HPWH and PVT?

asked 2015-10-21 14:28:33 -0500

s_pourm's avatar

updated 2017-05-04 06:59:18 -0500

Hi

The Heat pump water heater in Energyplus, Accept the Zone, Outdoor only, zone and outdoor, and scheduled as the input air node. In my model I have PVT which works as preheating. How can I connect the outlet node of PVT to HPWH, as its not the outdoor ,zone or scheduled?

Thanks, Navid

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2015-10-24 08:44:30 -0500

Archmage's avatar

I think you would have to use EMS. The PVT would need a dummy air handler connected to a dummy zone to get it to run. Then an EMS sensor on System Node Temperature would detect the temperature leaving the PVT and an EMS actuator would set the value of either a schedule value or an outdoor air node's temperature.

edit flag offensive delete link more

Comments

Thats really smart. I will try it today.Thank you. Currently I am producing the pvt outlet temperature out of E+ and using them as a schedule for heat pump inlet.

s_pourm's avatar s_pourm  ( 2015-10-24 09:06:45 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2015-10-21 14:28:33 -0500

Seen: 228 times

Last updated: Oct 24 '15