System sizing with ERV

asked 2015-10-21 12:13:24 -0600

ngkhanh's avatar

updated 2017-05-17 12:53:21 -0600

Hello I wonder how OS (E+) size the system with ERV ? I made a 1 zone PTHP with ERV sized for ventilation . The PTHP capacity did not change after add ERV system. In pratice, we can use ERV to reduce PTHP size - we could do like this in OS E+ by autosizing, could not we ? Thanks

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2015-10-21 12:44:53 -0600

Did you turn the OA on the PTHP off when you added the ERV? The PTHP size will not change if it and the ERV are both supplying the zone with OA. Below is an image of turning the OA off in OpenStudio, the inputs should be the same in E+.

image description

edit flag offensive delete link more

Comments

Yes i did it. The ERV was selected for Ventilation requirement in Airloop and get exactly outdoor rate.

ngkhanh's avatar ngkhanh  ( 2015-10-21 14:42:06 -0600 )edit