Are there two different Timesteps in EnergyPlus?
Hello,
I am wondering if there are two different time steps (one for Plant i.e. HVAC and the other for the Zone) in EnergyPlus? if not is there a response time for the Plant to start Circulating conditioned air? if there is a response time How can I control it?
Any help will be greatly appreciated.
Sincerely,
Nadish Anand
Update:
Hello Amir and Eric, I am referring to the Following Data Plot:
Zone Air Temperature-1 min. Timestep
This is the plot of the Zone Air Temperature Data I have obtained from my EnergyPlus Simulation. I have an EMS Code that Controls the HVAC Operation with a Offset Temperature from the Heating and Cooling Setpoints. The offset Temperature here is 0.6 deg.C and the Heating Setpoint is 21.1 deg.C. Now as you can see from the plot the HVAC system is not starting operation as soon as (21.1-0.6) = 20.5 deg.C is hit by the Zone Air temperature. It takes a while (1-3 mins.) to start operation. I am wondering why this behavior is experienced and hence my earlier question.
Thank you once again.
Nadish
Troubleshooting this might be easier if you had the simulation report the HVAC system heating energy at 'detailed' reporting frequency.
Hello Eric,
Thank you for your answer previously and the comment. Yes the Reporting frequency is 'detailed', and my timestep is 1 minute, I am not sure why the HVAC turns on After 2-3 minutes of hitting the Setpoint-Toffset in heating Operation.
Nadish
If you are using 1 minute zone timestep, then there will not be any system timesteps because the shortest is 1 minute and the zone timestep is already there. It is usual for such EMS control to be lagged by one timestep because the sensors need to be updated before the control can take effect. But behavior varys depending on the EMS calling point that is used.
Hello Archmage,
First of all thank you for the comment. I appreciate your time. Secondly, I am using "BeginTimestepBeforePredictor" Calling point for my Program Calling Manager. Is this creating the lag? Or do I need to modify my sensors and actuators to stop the lag?
Nadish
The two calling points you might try to decrease the lag are EndOfZoneTimestepAfterZoneReporting and InsideHVACSystemIterationLoop. However it is unlikely that you can eliminate all lag. There isn't really anything that can be done with sensors and actuators.