Use measured airflow rate in DOAS?

asked 9 years ago

updated 9 years ago

I have the measured airflow rate with 1-minute interval (variable speed fan) for the DOAS system. Can EnergyPlus specify the airflow of the airloop or fan to match the measured airflow rate?

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
4

answered 9 years ago

updated 9 years ago

EnergyPlus will typically operate the fan to meet the load the system sees (either ventilation, heating, or cooling).

Since your DOAS operates only to meet the ventilation requirement, you can set the ventilation requirements using the DesignSpecification:OutdoorAir object's Outdoor Air Flow Rate Fraction Schedule Name field.

You can also set the flow rate of the fan directly using an EMS Actuator on the "Fan Air Mass Flow Rate".

Preview: (hide)
link

Comments

Thanks Neal, I was having problems with OA.

IgnacioFurnies's avatar IgnacioFurnies  ( 9 years ago )