EnergyPlus IdealLoadAirSystem vs. Internal Gains

asked 2015-08-26 09:56:58 -0600

gerald's avatar

updated 2015-08-29 18:02:57 -0600

I run a simulation with HVAC:Template:IdealLoadAirSystem with a constant heating setpoint 20°C (in January, max outside temperature 13°C). Then i calculatet - from the Zone Ideal Loads Zone Total Heating Energy the - the required Energy in Watt. Imported that file through schedule:File and add "ElectricEquipment" with schedule Name (the name from schedule:file) + delete the IdealLoadAirSystem.

The result I expacted: The zone air temperature is 20°C The result I get: The Electric Equipment Total Heating Energy is the same than the Ideal Zone Total Heating Energy. But the temperature i different (up to 2K). Has anybody an idea?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2015-08-26 10:41:42 -0600

Archmage's avatar

I would guess the ElectricEquipment has a radiative fraction so not all its heat is hitting the zone air. The part that hits surfaces as infrared radiation can conduct out the surfaces.