Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

only 1 chiller is used if autosizing chiller capacity

asked 9 years ago

updated 5 years ago

The cooling load of my project is 500 ton, I would like to use 2 chillers for my baseline case in OS1.7 so that each chiller is less than 300 ton. However, if I autosize the chiller, the part load ratio show that only 1 chiller will be used whose size is 500 ton. How should I change the control mode so that the load could distributed evenly to each chiller?

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
4

answered 9 years ago

updated 9 years ago

In this case, only one chiller is being used because both chillers are probably sized to meet the full load of 500 tons.

Every chiller, boiler, etc. object has a field for "Sizing Factor" which is used to allocate the design load across multiple pieces of equipment. This defaults to 1.0, and the autosizing does not have a way to check if there are multiple chillers or boilers present. The detailed inputs for the chillers in OpenStudio should give you access to set the Sizing Factor for each one. For example, if you want 2 chillers of equal size, then set the sizing factor of both chillers to 0.5. If the total design chiller load is 500 tons, then this would result in 2 chillers of 250 tons.

Preview: (hide)
link

Comments

@MJWitte, sorry my description may be confusing. I mean autosizing the capacity, not the sizing factor.

Yan's avatar Yan  ( 9 years ago )

If you set the chiller's sizing factor to 0.6, then a 500 ton size will come out as 300 tons.

Archmage's avatar Archmage  ( 9 years ago )

@MJWitte, I am not sure if my understanding is correct. Do you mean that in this baseline case, I should first check the cooling load, then divide 300 ton by the load and get a factor, finally input the factor into sizing factor?

Yan's avatar Yan  ( 9 years ago )

@MJWitte, or do you mean dividing 1 by number of chiller and use this result as sizing factor?

Yan's avatar Yan  ( 9 years ago )

@Yan, as @Archmage said the sizing factor is multiplied by the total design load. You can allocate the chillers any way that you want. 0.5 and 0.5, or 0.4 and 0.6, or 0.6 and 0.6 for some extra capacity. You don't need to do a preliminary run unless you have a target size you want to reach.

MJWitte's avatar MJWitte  ( 9 years ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 9 years ago

Seen: 358 times

Last updated: Aug 27 '15