can we get the temperature of the air around the outside of a roof surface?

asked 9 years ago

oat's avatar

updated 7 years ago

May I ask if EnergyPlus can output the temperature of the air around the outside of surface?

Is it the same as the outside surface temperature?

Or does EP assume that the temperature of the air around the entire building envelope is uniform and equals to the air temperature as specified in the epw weather file for a given hour?

I ask this is because I'm trying to model a PV panel as a shading surface put above the roof surface in close distance. I want to know if the temperature of the air between the PV panel and the roof surface is hot enough to affect the output efficiency of the PV panel, assuming a certain desired temperature range for optimal PV output.

Thanks!

Preview: (hide)

3 Answers

Sort by » oldest newest most voted
3

answered 9 years ago

updated 9 years ago

If you search in this page on simple PV you will find a section on Integrated Exterior Vented Cavity, which is one of 5 methods available to calculate module operating temperatures. This is will let you do building integrated PV with a naturally vented air cavity. I believe there is an example file installed with E+ as well.

If the user specifies “Integrated Exterior Vented Cavity” for this parameter, then the temperature result for the exterior cavity is used for the cell temperature. Also the energy exported from the baffle surface as electricity is deprecated using a source term in the baffle’s temperature modeling.

Preview: (hide)
link

Comments

Hi Which Example file you are referring to? I am having trouble to go through this approach.

s_pourm's avatar s_pourm  ( 9 years ago )

GeneratorswithPV.idf uses SURFACEPROPERTY:EXTERIORNATURALVENTEDCAVITY
ShopWithSimplePVT.idf uses SOLARCOLLECTORPERFORMANCE:PHOTOVOLTAICTHERMAL:SIMPLE

At first glance, didn't see an example that used both of these

David Goldwasser's avatar David Goldwasser  ( 9 years ago )

Thanks David In my model, I have a fan working with BIPV/T system, But I don't know how can I add that. are all the models based on natural ventilation?

s_pourm's avatar s_pourm  ( 9 years ago )

Thank you very much, David, for your advice.

oat's avatar oat  ( 6 years ago )
2

answered 9 years ago

The local outdoor atmospheric properties (temperature and wind speed) are calculated independently for each surface, zone, and outdoor air node. The calculations of these properties are described in the Engineering Reference here. These calculations can be controlled with coefficients of a Site:HeightVariation object.

The calculated properties can be output from the model by requesting the output variables described here.

Preview: (hide)
link

Comments

Thank you very much, Eric, for your detailed advice. Will take a look of the references you suggested.

oat's avatar oat  ( 6 years ago )
1

answered 9 years ago

NickC's avatar

updated 9 years ago

Hello Oat; I'm also interested in the answer to your question "...does E+ assume that the temperature of the air around the entire building envelope is uniform and equals to the air temperature as specified in the epw weather file for a given hour?"

My assumption was that E+ did not perform complex exterior air calcs (like finite element or finite volume solutions)...perhaps I am mistaken!

I was searching around in the E+ engineering reference and came across the following exterior surface object SurfaceProperty:ExteriorNaturalVentedCavity and felt it might be of use.

Preview: (hide)
link

Your Answer