Very low COP values for VRF cooling and heating
Hi,
Using OpenStudio, I am modeling an office space which is cooled and partially heated by a VRF system. The VRF system is linked to 3 terminals, each managing a different thermal zone. Since I only have access to minimal manufacturer data, most of the performance and capacity curves were made constant, with the exception of the ''VRFHeatEIRFT'' curve with coefficient 1 = 1.208 and coefficient 4 = -0.03344. Despite the calculated COP values according to my formulas ranging from 1.2 to 3.5 across the outdoor temperature range in heating and a constant COP value of 2.5 in cooling, OpenStudio returns COP values between 0.3 and 0.8 throughout the year.
Despite this problem, the VRF fulfills the cooling load. However, the resulting electrical consumption is exaggerated.
The defrost operation is set to ReverseCycle with a timed value of 0.05. Basin heater capacity was set to 0W, and all other capacity and EIR curves were set to coef 1 = 1, Coefs 2-6 = 0. Piping correction factors were reduced to 0. The unit is hard sized to 8320W in cooling and heating, with a cooling load reaching 2000 W and heating loads reaching 3000 W. COP values range between 0.06 and 0.65 in cooling and between 0.33 and 0.8 in heating .
What other factors impact the resulting COP? What could explain such low COP values, especially in heating?