EIRDefrost function for air-to-water heat pump

asked 2026-02-08 14:18:48 -0500

Abir Ahsan's avatar

updated 2026-02-09 10:01:17 -0500

Hello all, For air-to-water heat pump EIRDefrost is a function of outdoor wet bulb and dry bulb conditions (https://github.com/NatLabRockies/Ener...). My understanding is since HP is working in cooling mode for defrost, cooling curve EIR inputs may be more reasonable? Shouldn't EIRDefrost then be a function of EWT and ambient source temp (Air)? I am trying to understand why this is a function of outdoor wet bulb and dry bulb conditions in the current source code. Would appreciate if anybody has some idea about the rationale behind this. I will really appreciate if anybody can point to any available curvefits to see how this performance changes.

-Abir

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2026-02-13 19:46:26 -0500

updated 2026-02-13 19:52:42 -0500

I haven't tried to create the EIRDefrost curves and there is very little information documenting HP defrost operation. I can say that there is a frost layer on the outdoor coil so it really doesn't matter what the outdoor condition is during defrost because that outdoor air temperature is not the outdoor coil exterior condition. The frost layer insulates the coil from the outdoor condition. However, the outdoor dry-bulb and wet-bulb temperature does affect how much of a frost layer is present when defrost starts. That said, I don't see how any variable other than indoor WBT would be relevant (an indication of suction pressure/temperature) to EIR since the outdoor operating condition is fixed (outdoor coil is inside a frost layer and compressor head pressure would also be fixed). I suspect that the EIRDefrost curve is relatively flat wrt outdoor conditions since when the HP switches to cooling mode the outdoor coil operating condition is fixed and indoor WB temperature would be naturally low in winter but do not have any measured data to confirm that suspicion.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Question Tools

2 followers

Stats

Asked: 2026-02-08 14:18:48 -0500

Seen: 121 times

Last updated: Feb 13