Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

How to model a Hot Air Source in Energyplus.

asked 2025-06-29 09:27:17 -0600

updated 2025-06-30 10:28:25 -0600

Hi there, I want to model a waste hot air source. It will supply hot air to a Air to Air Heat exchanger. How to model this in Energyplus.

Also, the air source will be OutdoorAir. Or, other air source allowed in Energyplus?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2025-07-22 13:48:16 -0600

The EnergyRecoveryVentilatory object contains an air-to-air heat exchanger and can be used to pre-heat/cool incoming outdoor air. Is that what you're trying to model?

edit flag offensive delete link more

Comments

I am considering that I will direct the Hot air directly to a thermal Zone. It is similar to throwing exhaust air of compressor into a zone during winter.

meftah416's avatar meftah416  ( 2025-07-22 19:20:12 -0600 )edit

Where is the hot air coming from? You said the air source will be outdoor air. Is it coming from outside, or is it coming from a different thermal zone?

ericmartinpe's avatar ericmartinpe  ( 2025-07-23 08:36:20 -0600 )edit

The air is coming from exhaust of an Air Compressor. The zone where air compressor is situated is not considered into the modeling. I am seeking ways to incorporate that Hot exhaust air into a room for heating purpose. How can I model that? If I consider it as Outdoor air, then how to make sure a high temperature air is coming? It should be turned off during summer. That means I need to have fresh outdoor air intake during summer. Alternatively, if I have an AirLoop with fan, how can I heat the supply air using a air-to-air heat exchanger. One side supply air, other side hot air from compresor

meftah416's avatar meftah416  ( 2025-07-23 08:51:23 -0600 )edit
1

I would model an unconditioned zone for where the air compressor is located and use an OtherEquipment object to characterize the heat gains from the compressor. Then, use ZoneMixing to simulate the interaction between the two zones.

ericmartinpe's avatar ericmartinpe  ( 2025-07-23 09:07:49 -0600 )edit

That is a wise way to do. Thanks for the idea. I will try that.

In the mean time, I edited the comments and add second question.

meftah416's avatar meftah416  ( 2025-07-23 09:12:19 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Question Tools

2 followers

Stats

Asked: 2025-06-29 09:27:17 -0600

Seen: 206 times

Last updated: Jul 22