Trouble using VRF components from the BCL in OpenStudio app v1.9

asked 2025-06-15 20:17:40 -0500

pmck's avatar

updated 2025-06-16 09:10:58 -0500

Hello,

I'm encountering an issue with OpenStudio application v1.9. I've downloaded components directly from the BCL within the application, but some aren't working as expected. For instance, I can drag and drop a VRF system from the library, but I'm unable to add the VRF zone terminal from the library.

Has anyone experienced this or know how to resolve it?

Thank you.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2025-06-19 07:52:43 -0500

updated 2025-06-19 13:30:25 -0500

Both the DAIKINREYQ 72 and the Fake VRF Outdoor Unit Example 2 outdoor units (from BCL) work with the default VRF indoor unit that comes with the App - tested with App 1.6.0, 1.8.0 & 1.9.0.

You should try out the Mitsubishi outdoor/indoor units, developed by @Ski90Moo. They are indeed available from BCL, but the lot gets lumped as a single terminal unit/component via BCL:

image description

Instead, add the downloaded Mitsubishi library osm as one of your default libraries (App Preferences > Change Default Libraries). Works for App 1.9.0.

image description

Couldn't get any of the LG units from BCL to work. These may no longer be supported:

  • GitHub repo is no longer available
  • designed for v1.9.0 ... SDK? App?.

However, a similar solution to the Mitsubishi units may work. I downloaded its .osc file, changed its extension to .osm, and also added it as a default library. I could drag and drop both outdoor and indoor LG units, but encountered FATAL errors when trying to run a simulation. The eplusout.err feedback is very informative, but I haven't taken a deep dive to debug the setup at this stage.


edit flag offensive delete link more

Comments

1

Hi Denis,

Thank you sir for your very helpful information!

I can confirm that both the DAIKINREYQ 72 and the Fake VRF Outdoor Unit work with the default VRF indoor unit. I also tried the outdoor LG units with the default VRF indoor unit, but, as you mentioned, I encountered "FATAL" errors when trying to run a simulation. Thanks again for your help!

pmck's avatar pmck  ( 2025-06-19 11:05:28 -0500 )edit

Good to know. Have you tried the Mitsubishi units (added as a default library)? These work.

Denis Bourgeois's avatar Denis Bourgeois  ( 2025-06-19 13:21:43 -0500 )edit
1

Yes sir, The Mitsubishi units worked perfectly when added as a default library. I genuinely appreciate your detailed guidance and assistance with this matter.

pmck's avatar pmck  ( 2025-06-19 23:50:05 -0500 )edit
1

Super! Great work @Ski90Moo. If you found the answer satisfactory, it is customary to accept it by clicking on the checkmark. Helps others in the future.

Denis Bourgeois's avatar Denis Bourgeois  ( 2025-06-20 04:38:00 -0500 )edit
1

Thank you. Yes, you can get the LG objects to work, but you will need to do some editing to the curves (OS:Table:Lookup). Some of the LG lookup tables are missing a field. For example, the !- Heating Capacity Ratio Modifier Function of Low Temperature Curve Name only has Output Values up to 119. The independent variables have 8 and 15 values, so the total dependent variables (output values) should be 8*15=120. They count up in groups of 15 at which point it starts with a low number and starts counting up again, so you should be able to spot where it is missing.

Ski90Moo's avatar Ski90Moo  ( 2025-06-20 08:40:20 -0500 )edit