how can I apply airflow network with ideal air loads?

asked 2025-04-22 21:34:52 -0500

updated 2025-04-23 09:13:21 -0500

Hi all,

I activated the airflow network in EP and used a schedule for when windows should be open (at 25°C), and I also have an ideal air load with cooling and heating schedules. The purpose of that was to examine the benefits of natural ventilation (AFN) in minimizing the cooling loads. The cooling and heating loads that resulted from this were very unrealistic! I have been reading previous posts and EP documentation, but I couldn't understand how to activate mixed mode using AFN with ideal air load. I applied ideal air load, as I am not a mechanical engineer and am still not much familiar with how to apply HVAC in OpenStudio or EnergyPlus. I appreciate your help in this!

edit retag flag offensive close merge delete

Comments

1

A few links on AFN vs IdealLoads: here, here, here. I suspect EMS will be required, e.g. overriding heating/cooling setpoints f(opening area).

Denis Bourgeois's avatar Denis Bourgeois  ( 2025-04-23 07:52:53 -0500 )edit

Have you looked at the zone temperatures, supply air heating/cooling energy, and AFN ventilation rate outputs? They might help you understand what's going on. A common issue for example is that the ventilation could be running at the same time as the heating, causing the loads to blow out. Here's some detailed discussions on AFN ventilation controls if that causes you problems.

Jamie Sullivan's avatar Jamie Sullivan  ( 2025-04-23 17:42:10 -0500 )edit

Thanks Denis and Jamie. You are right; the AFN is running while the IAL is being used. I've gone through Ep documentation again, and I found " HybridVentilaion" system manager, I think I need to use this one if I require the natural ventilation to be off once the operative temperature is not within the 80% adaptive model threshold upper and lower limits; otherwise, EP would not turn off AFN or wind and stack open area if ideal air load is on.

wala.beliah@research.uwa.edu.au's avatar wala.beliah@research.uwa.edu.au  ( 2025-04-23 20:25:12 -0500 )edit

Mmm, that might work but I'm inclined to think it won't. In my experience the "clashes" happen because the ventilation from the open windows can be incredibly strong with the AFN. The result of this is something like:

  1. Temperature rises above ventilation setpoint
  2. AFN opens the windows, applying something like >70ACH for one timestep
  3. This is enough ventilation to drop the zone air temperature below the heating setpoint
  4. Ventilation stops, and heating begins in the next timestep
  5. Repeat

So the heating and AFN are "technically" never on at the same time, but in practice clash

Jamie Sullivan's avatar Jamie Sullivan  ( 2025-04-23 21:00:27 -0500 )edit

Here in Brazil we use the NBR15575 standard to determine the thermal performance of the building, naturally ventilated and with conditioned ventilation. I have a small .pdf file that can help you, but it is written in Portuguese. I made it as a guide when I use E+ (Version 9.6.0) I can only upload directly to an answer reply. Is it OK? even though it is not (perhaps) an answer to your question.

Fred's avatar Fred  ( 2025-04-26 09:13:22 -0500 )edit

1 Answer

Sort by » oldest newest most voted
0

answered 2025-05-05 07:48:42 -0500

Fred's avatar

updated 2025-05-05 07:51:58 -0500

Hope it makes sense to you. More information can be obtained in these video lessons on NBR15575 training, especially lesson 7 that instructs how to treat the results obtained in the simulations.

https://www.youtube.com/watch?v=siHkl...

You can get lots of informatio at https://labeee.ufsc.br/pt-br

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2025-04-22 21:34:52 -0500

Seen: 230 times

Last updated: May 05