Cooling Tower is storing excess heat the majority of the time
I am getting following errors in my EnergyPlus Simulation, i need help in this matter. Note: My file is DOE Medium Sized Reference Building, i have changed HVAC System from air based to water based according to DOE Large Sized Reference Building.
Pictures Attached in pdf file on link https://drive.google.com/file/d/1A8LD...
* Warning * Plant Loop: TOWERWATERSYS Demand Side is storing excess heat the majority of the time.
* Warning * Plant Loop: TOWERWATERSYS Supply Side is storing excess heat the majority of the time.
It's possible the cooling tower can't not meet the setpoint for most of the time as your "approach" is 0. Try set the Offset Temperature Difference to be 7F, to allow the cooling tower meet the setpoint.