First time here? Check out the Help page!

Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Correct settings for setback temperature in DesignBuilder

asked Feb 21

AadriaanW's avatar

updated Feb 22

I have a DesignBuilder model made by someone else where we have an occupancy temperature and setback temperature in a zone that is not being followed. In the results we see that the temperature is always the occupancy temperature and never setback even though we have times where this should apply. We managed to activate it by setting the HVAC schedule to 0.5 for the time that there is no occupancy.

My question is: What is the correct way to activate the setback temperature? In my understanding it always works if in either Simple or Detailed HVAC the schedule for the HVAC system is "On 24/7" and you have an occupancy schedule where there is no occupancy (0 during x amount of time). From what I have seen this works with varying temperatures that I would expect with these 2 temperature settings, but now I am not sure. If this method doesn't work it means I will always have to make a seperate HVAC schedule to ensure the setpoints are being followed which just seems like a lot of extra work to me. Has anyone experienced this issue and what is the adviced solution?

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
4

answered Feb 23

Greg Estep's avatar

In DesignBuilder, the HVAC schedule (0=off,0.5=setback, 1= setpoint) is the way to do this. This is for detailed HVAC (simple activity data).

If you want more granular temperature control (beyond setpoint and setback) you will need to use detailed HVAC, detailed activity data.

The occupancy schedule does not control the HVAC temperature schedule. It is separate. if you have the HVAC schedule at "on 24/7" the temperature setpoint will be at setpoint at all times.

Yes, you will always have to make a separate HVAC schedule. This is more realistic than a simple occupancy schedule. For example, in an office, as the occupancy varies throughout the main work day, you want the office temperature to be at setpoint all day, then go to setback after hours.