Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Why Does the Air-Cooled Chiller Show a Higher COP Than the Water-Cooled One?

asked 2025-02-06 05:45:00 -0500

I'm comparing the COP of air-cooled and water-cooled chillers using the COMNET EIRFPLR curves

I plotted both chillers' COP using Desmos for both scroll type chillers:

image description

Given that both chillers have the same nominal COP (1 in this case), I expected the water-cooled chiller to perform better. However, the curve suggests that the air-cooled chiller has a higher COP across all part-load conditions.

This seems counterintuitive since water-cooled chillers are generally known to be more efficient. Am I misunderstanding something about the EIRFPLR curves, or is there another explanation for this result?

I want with this post suggestion for converting EIRFPLR to COP using this post

Would love to hear your insights! ๐Ÿš€

edit retag flag offensive close merge delete

Comments

EIR means energy input ratio, this is the inverse of COP. That might explain it. Instead of plotting COP, did you plot EIR?

Greg Estep's avatar Greg Estep  ( 2025-02-06 12:22:47 -0500 )edit

i went with the explanation given by @ericringold in this post assuming nominal EIR as 1 the hourly EIR is EIRFPLR/PLR and so the cop must be PLR/EIRFPLR. the formula are written in the left-most side of the image where x represents the PLR.

tomer@urecsys.com's avatar tomer@urecsys.com  ( 2025-02-06 13:03:21 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
2

answered 2025-02-07 04:25:03 -0500

PmP's avatar

Your f2 has an extra x multiplying the 1st parameter

edit flag offensive delete link more

Comments

oh man i sat on this for so much time, well thank you hahaha. the post may be deleted i guess

tomer@urecsys.com's avatar tomer@urecsys.com  ( 2025-02-07 05:08:13 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Sponsor

Training Workshops

Question Tools

2 followers

Stats

Asked: 2025-02-06 05:45:00 -0500

Seen: 378 times

Last updated: Feb 07 '25