zoneHvac Ideal loads

asked 2025-01-03 09:14:32 -0600

updated 2025-01-03 11:00:05 -0600

How do I adjust the ZoneHVAC:IdealLoadsAirSystem as the following: 

  • Zone heating set point air temperature: 20C 
  • Zone cooling set point air temperature: 24C
  • schedule availability for heating: 1 December until 31 march
  • schedule availability for Cooling: 1 april until 31 November  
  • heating default COP: 3WW
  • cooling default COP: 3WW

I am using the V9-4-0 IDF file

Help will be very appriciate

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2025-01-07 07:39:23 -0600

Zone heating and cooling setpoint temperature schedules are linked to zones through ZoneControl:Thermostat and e.g. ThermostatSetpoint:DualSetpoint objects. They indeed inform a ZoneHVAC:IdealLoadsAirSystem, yet they are defined separately.

Here's an example of seasonal heating vs cooling setpoint schedules. Hint: you can always adjust the heating & cooling setpoints to mimic ZoneHVAC:IdealLoadsAirSystem seasonal heating & cooling availability schedules, e.g.:

  • increase cooling setpoint to 60°C during winter
  • lower heating setpoint down to 5°C during summer

One can't define COPs for ZoneHVAC:IdealLoadsAirSystem. The latter provides an estimation of what an HVAC system needs to supply - not what is consumes. This is well stated here.