cooling tower and condenser pump are not functioning properly

asked 2024-12-30 04:11:37 -0600

Yun's avatar

updated 2024-12-31 01:38:59 -0600

In my EnergyPlus simulation, I’m sure there are no errors in the connections of branch, branchlist, and node. I’ve also set up the related schedules, including CondenserLoop, CondenserEquipmentOperationSchemes, CondenserEquipmentList, and PlantEquipmentOperation:CoolingLoad.

However, the results of the simulation shows that the energy consumption of cooling tower and condenser pump are both zero. This might mean that the two equipment is not functioning, and hence leads to zero energy consumption. Could you please suggest what might lead to this situation? The energy consumption of the two equipment should not be zero. Thank you.

This is the .svg file of condenser loop. image description

CondenserLoop,
Condenser Loop_Chiller,  !- Name
Water,                   !- Fluid Type
,                        !- User Defined Fluid Type
Condenser Loop_Chiller_Operation,  !- Condenser Equipment Operation Scheme Name
Condenser Loop_Chiller_Supply Side Outlet Branch Pipe Outlet Node,  !- Condenser Loop Temperature Setpoint Node Name
50,                      !- Maximum Loop Temperature {C}
5,                       !- Minimum Loop Temperature {C}
0.61185,                 !- Maximum Loop Flow Rate {m3/s}
0,                       !- Minimum Loop Flow Rate {m3/s}
autocalculate,           !- Condenser Loop Volume {m3}
Condenser Loop_Chiller_Supply Side Inlet Branch Pipe Inlet Node,  !- Condenser Side Inlet Node Name
Condenser Loop_Chiller_Supply Side Outlet Branch Pipe Outlet Node,  !- Condenser Side Outlet Node Name
Condenser Loop_Chiller_Supply Side Branches,  !- Condenser Side Branch List Name
Condenser Loop_Chiller_Supply Side Connectors,  !- Condenser Side Connector List Name
Condenser Loop_Chiller_Demand Side Inlet Branch Pipe Inlet Node,  !- Demand Side Inlet Node Name
Condenser Loop_Chiller_Demand Side Outlet Branch Pipe Outlet Node,  !- Demand Side Outlet Node Name
Condenser Loop_Chiller_Demand Side Branches,  !- Condenser Demand Side Branch List Name
Condenser Loop_Chiller_Demand Side Connectors,  !- Condenser Demand Side Connector List Name
SequentialLoad,          !- Load Distribution Scheme
None;                    !- Pressure Simulation Type


CondenserEquipmentOperationSchemes,
Condenser Loop_Chiller_Operation,  !- Name
PlantEquipmentOperation:CoolingLoad,  !- Control Scheme 1 Object Type
Condenser Loop_Chiller_Scheme 1,  !- Control Scheme 1 Name
On 24/7;                 !- Control Scheme 1 Schedule Name

CondenserEquipmentList,
Condenser Loop_Chiller_Scheme 1 Range 1 Equipment List,  !- Name
CoolingTower:SingleSpeed,!- Equipment 1 Object Type
CT-A1,                   !- Equipment 1 Name
CoolingTower:SingleSpeed,!- Equipment 2 Object Type
CT-A2,                   !- Equipment 2 Name
CoolingTower:SingleSpeed,!- Equipment 3 Object Type
CT-A3;                   !- Equipment 3 Name

PlantEquipmentOperation:CoolingLoad,
Condenser Loop_Chiller_Scheme 1,  !- Name
0,                  !- Load Range 1 Lower Limit {W}
1000000000000000.00,     !- Load Range 1 Upper Limit {W}
Condenser Loop_Chiller_Scheme 1 Range 1 Equipment List;  !- Range 1 Equipment List Name
edit retag flag offensive close merge delete

Comments

@Yun can you explain what you mean by "my cooling tower and condenser pump are not functioning properly"? Is the plant loop not meeting setpoint, not following flow rate control, etc.?

Aaron Boranian's avatar Aaron Boranian  ( 2024-12-30 09:37:30 -0600 )edit

@Aaron Boranian Sorry for not making it clear. "My cooling tower and condenser pump are not functioning properly" means that the cooling tower and condenser pump have not been turned on throughout the entire year, with a power consumption of 0.

Yun's avatar Yun  ( 2024-12-30 21:37:06 -0600 )edit

1 Answer

Sort by » oldest newest most voted
1

answered 2024-12-31 12:09:20 -0600

I would try placing the cooling tower supply pumps just upstream before the cooling towers on the supply side of the condenser water system (similar to how the chilled water supply pumps are just upstream before the chillers on the supply side of the chilled water system). The cooling tower supply pumps are currently placed on the demand side of the condenser water system, so EnergyPlus may not be properly able to turn them on to meet cooling tower loads.

This is based on the recommendation to place a single pump on the first supply-side branch, from the Engineering Reference section for Plant/Condenser Supply Side:

As previously discussed, the pump establishes the total loop mass flow rate by setting the flow in the first supply side branch.

edit flag offensive delete link more

Comments

Thank you so much, I solve my problem.

Yun's avatar Yun  ( 2025-01-01 23:35:35 -0600 )edit