BEopt: 3rd ed. Manual J/S HP Sizing

asked 2024-12-10 07:33:31 -0600

jpierce's avatar

updated 2024-12-11 11:54:20 -0600

Manual S was updated in late 2023 to allow for saner sizing of heat pumps in colder climates using N.2.3.4.2 "Variable-capacity equipment sizing condition: advanced" Will BEopt3's sizing algorithm be updated accordingly?

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
2

answered 2024-12-10 13:55:12 -0600

Yes, it's on our radar. We're hoping to incorporate it in OpenStudio-HPXML later this year, which would make it available in a subsequent BEopt release.

edit flag offensive delete link more
1

answered 2024-12-16 16:58:42 -0600

sashadf1's avatar

As Scott mentioned, it is planned. OS-HPXML would likely have an additional field for HeatPumpSizingMethodology (and potentially also HeatPumpBackupSizingMethodology), and the methods would be named to distinguish between the two.

HeatPumpSizingMethodology:ACCA vs. HeatPumpSizingMethodology:ACCA2023, or something like that.

See https://openstudio-hpxml.readthedocs.... for what OS-HPXML currently uses.

There are some challenges with implementing N.2.3.4 - Variable Capacity (either Advanced or Dry) because of the "minimum compressor cooling size factor" stipulations. I believe our current OS-HPXML implementation doesn't define this variable, as it is new to ACCA Manual S 2023. We will start by addressing the "Standard Sizing Condition" update for single and 2-speed equipment, which may be just updated oversize/undersize limits.