Primary and Secondary Loop Configuration for HEX and WaterHeater:Mixed

asked 2024-11-18 09:19:52 -0600

Behnam's avatar

updated 2024-11-18 09:43:08 -0600

Hi EnergyPlus Community,

I am trying to simulate two distinct loops, one primary and the other secondary, for space heating for a simple house. The Primary loop, has an HP EIR connected with a BaseBoard to provide the heating load for the house, for a specified time of a day. Additionally, this HP EIR has connected with a Fluid-Fluid heat exchanger in the demand, where this heat exchanger provides the heat for the secondary loop.

In the Secondary loop, there is a simple WaterHeater:Mixed connected with another BaseBoard to provide heating load for another specific time of the day.

When the BaseBoard of the primary loop is not working, the HP EIR should charges the WaterHeater:Mixed, which is used as a buffer water tank. This heat transaction is done via that heat exchanger.

The main challenge is the connection between the Primary Loop and the Secondary via the heat exchanger working as the medium.

*In the OpenStudio, I cannot find a way to specify the supply (inlet and outlet) and the use (inlet and outlet) for the WaterHeater:Mixed.*

What I could get are the below pictures:

Primary Loop: image description

Secondary Loop: image description

But this impose many challenges to modulate charge and discharge and SOC of the tank. Since these two loops should be completely separated and the heat exchanger is just a medium.

The loops that I need to develop seems such like below pictures:

Desired Primary Loop: image description

Desired Secondary Loop: image description

Could you kindly let me know how I can tackle this challenge?

Is there any specific configuration in OpenStudio to have this desired setup?

Do you have any similar example that I can inspire from?

Thank you very much in advance for your time and help.

Sincerely, Behnam

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2024-11-18 12:10:32 -0600

Greg Estep's avatar

updated 2024-11-18 12:12:02 -0600

Regarding,
"Additionally, this HP EIR has connected with a Fluid-Fluid heat exchanger in the demand, where this heat exchanger provides the heat for the secondary loop."

Set the fluid-fluid HX model type to Ideal and set the control type of your choice. Probably heating setpoint modulated, and place a setpoint manager just downstream of the supply side of the HX for the desired temperature. When the demand side of the secondary loop calls, the HX will modulate the demand side (primary) flow to meet the supply setpoint.

edit flag offensive delete link more

Comments

I followed that procedures: the model type, setpoints, etc, before. The question I have is related to the desired topology I am interested to employ for the loops (Primary, medium, and the Secondary)

Behnam's avatar Behnam  ( 2024-11-18 15:37:15 -0600 )edit