How Does EnergyPlus Determine When Refrigeration Compressors Start or Stop in a Parallel System?

asked 2024-11-08 06:12:45 -0600

Marcos's avatar

updated 2024-11-08 10:17:57 -0600

Hi everyone,

I'm setting up a refrigeration system in EnergyPlus, and I see that it allows you to define a list of compressors that work in parallel. My question is: how does EnergyPlus decide when each compressor in the parallel setup should start or stop functioning?

Does it use any specific control strategy or thresholds based on temperature, load, or any other conditions to activate or deactivate individual compressors?

Thanks in advance for any insights!

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2024-11-11 05:51:40 -0600

PmP's avatar

Here is a link to the documentation: https://bigladdersoftware.com/epx/doc...

The quote appears twice, one for normal refrigeration systems and another time for CO2 transcritical systems: "Once the corrected capacity is calculated for each compressor, the compressors are dispatched one at a time until the system load is met. The last compressor dispatched is assumed to run at full load for the fraction of the time step necessary to meet the load, That is, the model neglects compressor cycling losses at part-load conditions. "

Thus the answer to your question is there is no control strategy nor thresholds based on anything but load, they work from first to last from partial to full power.

edit flag offensive delete link more