thermal zones end uses [closed]
I have a building consisting of 3 apartments distributed across 3 floors. I used Ideal Air Loads for simplifying the HVAC system, but when I check the results in OpenStudio Results, the energy consumption associated with each thermal zone I defined does not appear. How can I resolve this?
Duplicate of this post.