HVAC sizing Openstudio

asked 2024-09-28 07:56:49 -0500

OlivierC37's avatar

updated 2024-09-29 20:01:43 -0500

Hello, I have Openstudio version 1.8.0 and I don't understand what I have to do in the “Thermal Zone” section so that I can have the air-conditioning and heating powers to set up after selecting “Run simulation”. 2 years ago, in the “Thermal Zones” section, I know that I had to drag and drop CLG HVAC in the “Cooling Thermostat schedule” section and HTG HVAC in the “Heating Thermostat schedule” section, then run the simulation. I just need to be able to size the heating and cooling capacities I'll need to install in my building. Can anyone help me?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
2

answered 2024-09-28 10:01:03 -0500

JS66's avatar

I would recommend utilizing the ZoneHVAC:IdealLoadsAirSystem. In the OpenStudio interface, there should be a check mark by each thermal zone to turn on ideal air system. In addition, each thermal zone will need a ZoneControl:Thermostat for cooling and heating. If you load in a common library, there should be a schedule for each like you mentioned.

Before running the simulation, I would recommend adding internal loads and outside air requirements (DesignSpecification:OutdoorAir). A weather file and design day data will also be needed to run the simulation.

Before running the simulation, I would recommend reading the following links (ideal air loads, and simulation control: https://bigladdersoftware.com/epx/doc... https://bigladdersoftware.com/epx/doc...

edit flag offensive delete link more

Comments

Hello, Thank you for your help, but where can I find ZoneControl:Thermostat for cooling and heating? And how I can add it on openstudio? In addition, how and where I can add internal loads and outside air requirements? I'm not comfortable with or familiar with the workings of Openstudio. If you can provide screenshots, that would be very useful.

Thanks in advance

OlivierC37's avatar OlivierC37  ( 2024-09-28 11:12:24 -0500 )edit
1

I would recommend reading the "internal loads" and "Design Specification Outdoor Air" section of this website. The youtube video will show you how to set up ideal air loads. Running an older version of OpenStudio may not be exactly the same, but it will be very similar.

https://openstudiocoalition.org/getti...https://www.youtube.com/watch?v=SYTLq...

JS66's avatar JS66  ( 2024-09-28 11:19:18 -0500 )edit

Thanks a lot for your help, its' working

OlivierC37's avatar OlivierC37  ( 2024-09-29 04:08:35 -0500 )edit