Hello EnergyPlus users and developers,

I need to ask a question about modeling two different HVAC systems for a super-duper simple SINGLE zone/space. Let’s say one is [HP+Electrich SHW] and the other [VAV+Gasboiler SHW]. I am interested in having the first one ([HP+Electric SHW]) to be operable from 7:00 to 16:00 and the other system ([VAV+Gasboiler SHW]) from 16:00 to 7:00. In the end, I should have one integrated result for the zone operative temperature and all the loads.

I would appreciate it if you could kindly let me know how I can perform this simulation.

Thanks very much in advance.

Sincerely, Behnam

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2024-09-20 13:47:15 -0500

You can attach multiple HVAC equipment (whether zonal equipment, airloop HVAC, etc.) to the ZoneHVAC:EquipmentList object. This object defines all HVAC equipment serving the zone.

To specify the operation, you could then:

  • Set the load distribution scheme to "SequentialLoad"
  • Define Sequential Heating/Cooling Fraction Schedules, so that one system has 1s between 7:00-16:00 and 0s elsewhere, and the other system has 1s between 16:00-7:00 and 0s elsewhere.

(Alternatively, you could probably set the Sequential Heating/Cooling Fraction Schedules to constant 1s, and then use availability schedules on the equipment themselves to define their operation.)