One way of working around that could be to also schedule the setpoints - set the cooling setpoint higher when it's not supposed to be being used, and the heating setpoint lower when it's not supposed to be being used.
edit: using Dual Setpoint you should be able to do this like so:
ThermostatSetpoint:DualSetpoint,
setpoints1, !- Name
Heating, !- Heating Setpoint Temperature Schedule Name
Cooling; !- Cooling Setpoint Temperature Schedule Name
Schedule:Compact,
Heating,
Through: 03/31,
For: AllDays,
Until: 24:00, 22.78,
Through: 10/20,
For: AllDays,
Until: 24:00, 20,
Through: 12/31,
For: AllDays,
Until: 24:00, 22.78;
Schedule:Compact,
Cooling,
Through: 06/30,
For: AllDays,
Until: 24:00, 25,
Through: 09/15,
For:AllDays,
Until: 24:00, 22.22,
Through: 12/31,
For: AllDays,
Until: 24:00, 25;
Fill in setpoint values as desired. You could try to set it up to swap between single heating and single cooling, but I think that would be more complicated and not really add anything? Unless someone who knows more about the fine details of the systems says otherwise...
