This is only a partial diagnosis of your question.
Right now your chiller is set to constant flow, in the .idf:
ConstantFlow, !- Chiller Flow Mode
And your setpoint manager is controlling the outlet temperature, keeping it fixed at 5oC (Actually I think the setpoint is set at 0.5oC but the minimun loop temperature forbids it from going lower).
With constant flow and fixed outlet (Impulsion) temperature, the only variable for the heat balance to satisfy the demand is changing the return temperature. (In Q=mSpDT; m=cte; Sp=cte; DT=T_return-5).
Here is the input output guide of the chiller for other modes of modulation: https://bigladdersoftware.com/epx/docs/24-1/input-output-reference/group-plant-equipment.html#field-chiller-flow-mode
Two possible solutions I can think of:
If you find a solution that works, I encorage you to post it here!
Good luck with your simulations, PMP