With regards to the EnergyPlus side of the model, scheduling the VRF terminal units should be performed using the coil availability schedules. Using the thermostat temperature schedule to dictate operation (i.e., 74F otherwise 100F) will lead to the heating coil turning on when the system is expected to be off. Use a People and Equipment should be associated with their own independent schedules. See the VariableRefrigerantFlow_5Zone.idf example file for more information.
ZoneHVAC:TerminalUnit:VariableRefrigerantFlow,
TU1, !- Zone Terminal Unit Name
VRFAvailSched, !- Terminal Unit Availability Schedule
Example Availability Schedule:
Schedule:Compact,
VRFAvailSched, !- Name
Fraction, !- Schedule Type Limits Name
Through: 3/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00,1.0, !- Field 3
Through: 9/30, !- Field 5
For: WeekDays, !- Field 6
Until: 7:00,0.0, !- Field 7
Until: 17:00,1.0, !- Field 9
Until: 24:00,0.0, !- Field 11
For: SummerDesignDay WinterDesignDay, !- Field 13
Until: 24:00,1.0, !- Field 14
For: AllOtherDays, !- Field 16
Until: 24:00,1.0, !- Field 17
Through: 12/31, !- Field 19
For: AllDays, !- Field 20
Until: 24:00,1.0; !- Field 21
ZoneControl:Thermostat,
SPACE1-1 Control, !- Name
SPACE1-1, !- Zone or ZoneList Name
Zone Control Type Sched, !- Control Type Schedule Name
ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type
DualSetPoint; !- Control 1 Name
DualSetPoint, !- Name
Htg-SetP-Sch, !- Heating Setpoint Temperature Schedule Name
Clg-SetP-Sch; !- Cooling Setpoint Temperature Schedule Name
With regards to the EnergyPlus side of the model, scheduling the VRF terminal units should be performed using the coil availability schedules. Using the thermostat temperature schedule to dictate operation (i.e., 74F otherwise 100F) will lead to the heating coil turning on when the system is expected to be off. Use a of People and Equipment should be associated with their own independent schedules. See the VariableRefrigerantFlow_5Zone.idf example file for more information.
Schedule:Compact,