DesignSpecification:OutdoorAir (DSOA) is primarily used for sizing (which ignores the schedule), but it can also be used for control in certain situations:
Controller:MechanicalVentilation references a DSOA for each zone on the system. This is the only way to control the central OA amount based on the schedule in DSOA.ZoneHVAC:IdealLoadsAirSystem and ZoneHVAC:HybridUnitaryHVAC use a DSOA reference to control OA flow for these single-zone systems.AirTerminal:SingleDuct:ConstantVolume:NoReheat, AirTerminal:SingleDuct:Mixer, AirTerminal:DualDuct:VAV:OutdoorAir use a DSOA reference to set a flow request from the central air system.For the example files 5ZoneFanCoilDOASCool_rev and 5ZoneWarmest_Rev, add a Controller:MechanicalVentilation object to control the central OA based on the schedule in the DSOA object.
For the example file VariableRefrigerantFlow_5Zone_rev, the OA flow rate for ZoneHVAC:TerminalUnit:VariableRefrigerantFlow cannot be scheduled. It will be one of three fixed amounts as specified in the "Cooling/Heating/No Load Outdoor Air Flow Rate" fields.
So, this is working as designed, even if it is a bit confusing. As general rule, DesignSpecification:OutdoorAir is only used by the objects which reference it directly.