You can change the airflow of your central fan by EMS. I modelled the EMS in the ExampleFile: VAVSingleDuctReheat_EMS.idf for reference. The revised idf file is here (V22-2-0). You can refer to it, especially the following part.
EnergyManagementSystem:Actuator,
Fan_Mass_Flow_Rate, !- Name
Var Vol Supply Fan 1, !- Actuated Component Unique Name
Fan, !- Actuated Component Type
Fan Air Mass Flow Rate; !- Actuated Component Control Type
EMSPCM_Fan_Flow_Change, !- Name
InsideHVACSystemIterationLoop, !- EnergyPlus Model Calling Point
EMSP_Fan_Flow_Change; !- Program Name 1
EMSP_Fan_Flow_Change, !- Name
IF (Hour >= 22) || (Hour <= 5), !- Program Line 1
SET Fan_Mass_Flow_Rate = 1.3 * 1.17742603470021 * 0.6, !- Program Line 2
ELSE, !- A4
SET Fan_Mass_Flow_Rate = 1.3 * 1.17742603470021, !- A5
ENDIF; !- A6
Output:EnergyManagementSystem,
Verbose, !- Actuator Availability Dictionary Reporting
Verbose, !- Internal Variable Availability Dictionary Reporting
None; !- EMS Runtime Language Debug Output Level
You may need to read EMS Application Guide if you are not familiar with EMS. The quickest way without understanding EMS is that you should change
Actuated Component Unique Name from "Var Vol Supply Fan 1" to the actual fan name in your model1.17742603470021 is the air density [kg/m3] for calculating Fan Air Mass Flow Rate. I thought either the standard air density at 20C and 1atm (1.204kg/m3) or System Node Current Density is used, but as long as I compared the simulation results of System Node Mass Flow Rate and System Node Current Density Volume Flow Rate, that "constant" number is always used in EnergyPlus. You can change the number if necessary.
Output:EnergyManagementSystem helps output edd file which includes actuators available in your model.
At first, I tried to change airflow of each AirTerminal, but the following EMS did not work.
Zone_1_VAV_Max_Mass_Flow_Rate, !- Name
Zone 1 Reheat Air Outlet Node, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Mass Flow Rate Maximum Available Setpoint; !- Actuated Component Control Type
Zone_2_VAV_Max_Mass_Flow_Rate, !- Name
Zone 2 Reheat Air Outlet Node, !- Actuated Component Unique Name
Zone_3_VAV_Max_Mass_Flow_Rate, !- Name
Zone 3 Reheat Air Outlet Node, !- Actuated Component Unique Name
EMSPCM_VAV_Max_Flow_Change_Not_Work, !- Name
EMSP_VAV_Max_Flow_Change_Not_Work; !- Program Name 1
EMSP_VAV_Max_Flow_Change_Not_Work, !- Name
SET Zone_1_VAV_Max_Mass_Flow_Rate = 0.47 * 1.17742603470021 * 0.6, !- Program Line 2
SET Zone_2_VAV_Max_Mass_Flow_Rate = 0.36 * 1.17742603470021 * 0.6, !- A4
SET Zone_3_VAV_Max_Mass_Flow_Rate = 0.47 * 1.17742603470021 * 0.6, !- A5
ENDIF; !- A6
I also tried to change the Fan Maximum Mass Flow Rate, but also did not work.
EnergyManagementSystem:InternalVariable,
Fan_Max_Mass_Flow_Rate, !- Name
VAR VOL SUPPLY FAN 1, !- Internal Data Index Key Name
Fan Maximum Mass Flow Rate; !- Internal Data Type
EMSPCM_Fan_Max_Flow_Change_Not_Work, !- Name
EMSP_Fan_Max_Flow_Change_Not_Work; !- Program Name 1
EMSP_Fan_Max_Flow_Change_Not_Work, !- Name
SET Fan_Max_Mass_Flow_Rate = 1.3 * 1.17742603470021 * 0.6, !- Program Line 2
ENDIF; !- A4
So, the only way I know is to change the fan flow rate (not the maximum fan flow rate). The fan changed fan flow rate becomes constant, but it's ok in your case as you said your system blows a constant amount of air. Btw, if that's the case, it's not VAV-System but CAV-System.
ELSE, !- A4
ENDIF; !- A6
ENDIF; !- A6
ENDIF; !- A4
SET Fan_Mass_Flow_Rate = 1.3 * 1.17742603470021 1.17742603469114 * 0.6, !- Program Line 2
ELSE, !- A4
SET Fan_Mass_Flow_Rate = 1.3 * 1.17742603470021, 1.17742603469114, !- A5
ENDIF; !- A6
Actuated Component Unique Name from "Var Vol Supply Fan 1" to the actual fan name in your model1.17742603470021 1.17742603469114 is the air density [kg/m3] for calculating Fan Air Mass Flow Rate. I thought either the Rate for this ExampleFile. The standard air density at 20C and 1atm (1.204kg/m3) or is 1.204kg/m3, but the air density is adjusted according to System Node Current DensityElevationis used, but as long as I compared the simulation results of System Node Mass Flow RateSite:Locationand in EnergyPlus/DesignBuilder. Please refer to this post, but the R (Gas Constant) in the post might be slightly different from what EnergyPlus actually uses. I consider R = 287.00461429615 so that the Air Terminal VAV Damper Position is reduced to exactly 60%. System Node Current Density Volume Flow RateElevation, that "constant" number of this ExampleFile is always used in EnergyPlus. You can change the number if necessary.190m, so the air density = 101325 * (1.0 − 190 * 0.0000225577)^5.2559 / (287.00461429615 * (20 + 273.15)) = 1.17742603469114 [kg/m3]
SET Zone_1_VAV_Max_Mass_Flow_Rate = 0.47 * 1.17742603470021 1.17742603469114 * 0.6, !- Program Line 2
SET Zone_2_VAV_Max_Mass_Flow_Rate = 0.36 * 1.17742603470021 1.17742603469114 * 0.6, !- A4
SET Zone_3_VAV_Max_Mass_Flow_Rate = 0.47 * 1.17742603470021 1.17742603469114 * 0.6, !- A5
ENDIF; !- A6
SET Fan_Max_Mass_Flow_Rate = 1.3 * 1.17742603470021 1.17742603469114 * 0.6, !- Program Line 2
ENDIF; !- A4
So, the only way I know is to change the fan flow rate (not the maximum fan flow rate). The changed fan flow rate becomes constant, but it's ok in your case as you said your system blows a constant amount of air. Btw, if that's the case, it's not VAV-System but CAV-System.