"Riding the pump curve" means the pump with constant speed drive operates at variable water flow rate. You should use Pump:VariableSpeed for the secondary pump, but you should be careful about the coefficients of the Part Load Performance Curve.
The coefficients are discribed in ANSI/ASHRAE/IES Standard90.1 Performance Rating Method Reference Manual.
The primary pump has a constant water flow rate. Pump:ConstantSpeed should be used.
Please refer to the input example below for each parameter.
Pump:ConstantSpeed,
chiller1 ChW Branch Pump,!- Name
chiller1 ChW Pump Inlet, !- Inlet Node Name
chiller1 Chw Inlet, !- Outlet Node Name
autosize, !- Design Flow Rate {m3/s}
75384, !- Design Pump Head {Pa}
autosize, !- Design Power Consumption {W}
0.9, !- Motor Efficiency
0, !- Fraction of Motor Inefficiencies to Fluid Stream
Intermittent, !- Pump Control Type
, !- Pump Flow Rate Schedule Name
, !- Pump Curve Name
, !- Impeller Diameter {m}
, !- Rotational Speed {rev/min}
, !- Zone Name
, !- Skin Loss Radiative Fraction
PowerPerFlowPerPressure, !- Design Power Sizing Method
, !- Design Electric Power per Unit Flow Rate {W/(m3/s)}
1.38888888888889, !- Design Shaft Power per Unit Flow Rate per Unit Head {W/((m3/s)-Pa)}
Chilled Water Pump; !- End-Use Subcategory
Pump:VariableSpeed,
CHWloop ChW Secondary Pump, !- Name
CHWloop ChW Demand Inlet,!- Inlet Node Name
CHWloop ChW Secondary Pump Outlet, !- Outlet Node Name
autosize, !- Design Maximum Flow Rate {m3/s}
150768, !- Design Pump Head {Pa}
0, !- Coefficient 1 of the Part Load Performance Curve
3.2485, !- Coefficient 2 of the Part Load Performance Curve
-4.7443, !- Coefficient 3 of the Part Load Performance Curve
2.5294, !- Coefficient 4 of the Part Load Performance Curve
autosize, !- Design Minimum Flow Rate {m3/s}
, !- VFD Control Type
, !- Pump RPM Schedule Name
, !- Minimum Pressure Schedule {Pa}
, !- Maximum Pressure Schedule {Pa}
, !- Minimum RPM Schedule {rev/min}
, !- Maximum RPM Schedule {rev/min}
, !- Zone Name
0.25, !- Design Minimum Flow Rate Fraction
