I do see a set point manager at the outlet of the HX. However, I do not see a set point at the AirLoopDOASSplitterInlet node.
SetpointManager:MixedAir,
HEX-1-1 Heat Recovery Air Temp Manager, !- Name
Temperature, !- Control Variable
AirLoopDOASSplitterInlet,!- Reference Setpoint Node Name
OA Supply Fan Inlet, !- Fan Inlet Node Name
AirLoopDOASSplitterInlet,!- Fan Outlet Node Name
HEX Supply Air Outlet; !- Setpoint Node or NodeList Name
Adding this set point manager did not correct the problem in V9.6.
SetpointManager:Scheduled,
OA Air Temp Manager 20, !- Name
OA Cooling Supply Air Temp Sch, !- Schedule Name
AirLoopDOASSplitterInlet; !- Setpoint Node or NodeList Name
I updated this file to V22.2 and there is some other problem in the file that I have narrowed down to the DOAS air loop but not quite sure what the problem is.
The error (in the debugger) is ** Severe ** invalid vector subscript
. This error is related to a bug where a HX in the DOAS air loop cannot autosize properly.
I corrected that problem and the simulation did run and now shows these errors with the set point managers.
** Warning ** SetpointManager:Scheduled="OA AIR TEMP MANAGER 1"
** ~~~ ** ...setpoint node conflicts with another setpoint manager.
** ~~~ ** ...conflicting setpoint manager = SetpointManager:MixedAir:"HEX-1-1 HEAT RECOVERY ECONOMIZER TEMP MANAGER"
** ~~~ ** ...conflicting node name = OA SUPPLY FAN INLET
** ~~~ ** ...control type variable = Temperature
** Severe ** CalcMixedAirSetPoint: Missing reference temperature setpoint for Mixed Air Setpoint Manager HEX-1-1 HEAT RECOVERY AIR TEMP MANAGER
** ~~~ ** Node Referenced =AIRLOOPDOASSPLITTERINLET
** ~~~ ** use an additional Setpoint Manager with Control Variable = "Temperature" to establish a setpoint at this node.
** Severe ** CalcMixedAirSetPoint: Missing reference temperature setpoint for Mixed Air Setpoint Manager HEX-1-1 HEAT RECOVERY ECONOMIZER TEMP MANAGER
** Fatal ** Previous severe set point errors cause program termination
I added back in the set point manager for the AirLoopDOASSplitterInlet node (the SPM above) and the simulation runs successfully. I am not quite sure why adding this set point manager in V22.2 worked while trying this same correction in V9.6 did not. I do believe there is a problem with autosizing the HX in V9.6 and you will have difficulty getting this configuration to run in V9.6. I would suggest removing the HX from the DOAS air loop until this can be corrected.