A little update as it might be useful for other users.
Neal's answer made sense the way he presented it. However, it didn't quite add up with the data I had. To find out what the calculation is in both cases, I generated hourly reports in both eQUEST and EnergyPlus. Here is what I found out:
Calculation of the fuel consumption in DOE-2:
  • Calculation of the PLR: PLR = (Load for the hour) / (Total Furnace Capacity)
  • Use the PLR to get the HIR f(PLR) using the performance curve attached to the system
  • Calculation of the operational HIR: HIR-op = HIR f(PLR) * HIR-rated
  • Fuel consumption: Qfuel = (Total Furnace Capacity) * HIR-op (eq. 1)
Here is an excerpt from an hourly report from eQUEST that illustrate the calculation:
In this example, the total furnace capacity is 39988 Btu/h and the rated HIR is 1.25.
Calculation of the fuel consumption in EnergyPlus:
  • Use the PLR to get the PLF f(PLR) using the performance curve attached to the system
  • Fuel consumption: Qfuel = (Total Furnace Capacity) * PLR * HIR-rated / PLF (eq. 2)
Here is an excerpt from an hourly report from EnergyPlus that illustrate the calculation:
Comparison:
Then, if we look at (eq. 1) and (eq. 2):
  • HIR f(PLR) * HIR-rated = PLR * HIR-rated / PLF
  • Which simplifies to HIR f(PLR) = PLR / PLF
  • Thus PLF = PLR / HIR f(PLR)
In conclusion PLF and HIR f(PLR) are not quite the same.
Using this relation I converted the curve used in eQUEST (by default) to the match the PLF used in EnergyPlus.
  • EnergyPlus PLF = f(PLR) is the default curve used in EnergyPlus
  • eQUEST PLF = f(PLR) is the default curve used in eQUEST converted to the EnergyPlus "format".
