I figured out the cause by comparing my model and HVACTemplate-5ZoneVRF.idf in ExampleFiles.
The cause was Maximum Outdoor Temperature in Heating Mode in HVACTemplate:System:VRF. The default value is 16ºC. However, if a value that is less than 26.5ºC is input, the WaterCooled VRF doesn't heat zones even when the actual outdoor temperature is much lower than the input value. This might be a bug.
This does not occur when AirCooled is selected as Condenser Type of VRF. The value in HVACTemplate-5ZoneVRF.idf is set to 30ºC (below image), and it runs fine. My model used default 16ºC.
This does not occur when AirCooled is selected as Condenser Type of VRF. The value is set to 30ºC in HVACTemplate-5ZoneVRF.idf is set to 30ºC (below image), and it runs fine. My model used default 16ºC.
This does not occur when AirCooled is selected as Condenser Type of VRF. The value is set to 30ºC in HVACTemplate-5ZoneVRF.idf (below image), and it runs fine. My model used default 16ºC.16ºC. When I changed it to 26.5°C or higher, my model started to heat zones in winter.
| 4 | No.4 Revision |
This does not occur when AirCooled is selected as Condenser Type of VRF. The value is set to 30ºC in HVACTemplate-5ZoneVRF.idf (below image), and it runs fine. My model used default 16ºC. When I changed it to 26.5°C 26.5ºC or higher, my model started to heat zones in winter.winter. Conversely, when I changed the value to less than 26.5ºC in HVACTemplate-5ZoneVRF.idf, the model stopped heating.