The changes to the Prototype Building Models (including the data center addition) are described here: Enhancements to ASHRAE Standard 90.1 Prototype Building Models. Here is the relevant excerpt:
2.1.1.2 IT Equipment Loads
Equipment in data centers typically includes servers, storage devices, network equipment, and uninterruptable power supplies ( UPS ). Literature review indicates the IT load density for core data centers usually lies between 30 and 60 W/ft2 for large office buildings (LBNL 2001 - 2004; Richman et al. 2008 ; NREL 2009 ). The IT closets are composed primarily of network equipment such as high power switches, routers, and UPS. In some cases, the IT closets can be small computer server rooms . Because there is no specific power density found in the literature for IT closets, we assume that the IT closets have power density at 20 W/ ft2, which is the minimum threshold value defined for computer rooms in Standard 90.1. Thus, the equipment load densities used are as follows:
- Core data center : 45 W/ft2 of IT load
- IT closets : 20 W/ft2
Additionally, based on looking at the IDF file, these loads are running ALWAYS_ON (24/7/365), and 100% of the heat gain is going into the zone, with 50% of the heat being sensible and the other 50% being radiant. The HVAC equipment must remove this heat to meet the heating setpoints. Here is the excerpt from the IDF file that shows the Core data center electric load:
ElectricEquipment,
DataCenter_Basement_MiscPlug_Equip, !- Name
DataCenter_basement_ZN_6,!- Zone or ZoneList Name
ALWAYS_ON, !- Schedule Name
Watts/Area, !- Design Level Calculation Method
0, !- Design Level {W}
484.423246742185, !- Watts per Zone Floor Area {W/m2}
, !- Watts per Person {W/person}
0.0000, !- Fraction Latent
0.5000, !- Fraction Radiant
0.0000, !- Fraction Lost
DataCenter_PlugLoads; !- End-Use Subcategory