FreeCoolingChiller.idf may help you with what you are looking for. Override Cooling Control Temperature Mode' in HeatExchanger:FluidToFluid should probably be set to 'DryBulbTemperature' and 'Free Cooler Outlet Node' should have different setpoint. For chilled water loop, everything else is probably fine. But for condenser loop you may also need EMS. Instead of 'SetpointManager:FollowOutdoorAirTemperature', condenser supply outlet node should have setpoint schedule which is modified based on outdoor air temperature something like below.
SetpointManager:Scheduled,
Condenser Loop Setpoint Manager, !- Name
Temperature, !- Control Variable
Cond Loop Temp Schedule, !- Schedule Name
Condenser Supply Outlet Node; !- Setpoint Node or NodeList Name
EnergyManagementSystem:Actuator,
Set_CondLoopTemp_Sched, !- Name
CondLoopTempSchedule, !- Actuated Component Unique Name
Schedule:Compact, !- Actuated Component Type
Schedule Value; !- Actuated Component Control Type
My Setpoint Schedule Calculator Example,
EndOfZoneTimestepBeforeZoneReporting,
Set_CondLoopTemp_Sched_Prog;
OutdoorTemp, !- Name
Environment, !- Output:Variable Index Key Name
Site Outdoor Air Drybulb Temperature; !- Output:Variable Name
Set_CondLoopTemp_Sched_Prog,
IF (OutdoorTemp >= 3.33),
Set Set_CondLoopTemp_Sched = 35 ,
ELSE,
Set Set_CondLoopTemp_Sched = 3 ,
ENDIF;
Output:Variable,CondLoopTempSchedule,Schedule Value,timestep;
CondLoopTempSchedule, Cond Loop Temp Schedule, !- Actuated Component Unique Name
ELSE,
ENDIF;
Schedule:Compact,
Cond Loop Temp Schedule, !- Name
Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,1; !- Field 3
ELSE,
ENDIF;
Output:Variable,CondLoopTempSchedule,Schedule Output:Variable,Cond Loop Temp Schedule,Schedule Value,timestep;
| 4 | No.4 Revision |
Schedule:Compact,
ELSE,
ENDIF;