In addition here are my two cents:
Always use the system recommended by the manufacturer of your VRV. eQuest can't model VRV properly, so manufacturers choose a given eQuest system and create custom curves for THIS system in order to approximate what's going on. That's why they give you a modeling guide and eQuest curves, so use that. It will also help you justify your approach if you're part of a code compliance or incentive program.
As far as heating going up with heat pump compared to elec, it's likely a modeling mistake and/or lack of analysis of the model's output (unmet hours in particular, maybe outdoor air as well). @Daniel's suggestions are on point and also where I would start to debug.
Always use the system recommended by the manufacturer of your VRV. VRV. eQuest can't model VRV properly, so manufacturers choose a given eQuest system and create custom curves for THIS system in order to approximate what's going on. That's why they give you a modeling guide and eQuest curves, so use that. It will also help you justify your approach if you're part of a code doing this for compliance or an incentive program.
Always use the system recommended by the manufacturer of your VRV. eQuest can't model VRV properly, so manufacturers choose a given eQuest system and create custom curves for THIS system in order to approximate what's going on. That's why they give you a modeling guide and eQuest curves, so use that. It will also help you justify your approach if you're doing this for compliance or an incentive program.
@crdugin just refreshed my memory. As of July 2014, there was still a mistake in Daikin's curves: eQuest has a limit of 80 characters per line... If you put more it gets truncated.
I emailed some rep twice about it, I don't know if it was corrected or not.
Here's a message I wrote in July 2014 to the eQuest user mailing list:
I've been trying to model a Daikin VRV system and trying to figure out why I was getting 100 times more space heating in the proposed (VRV) model compared to the baseline model (PTHP). After isolating the problem to the VRV, I found a conversation from March 2014 between a few folks (Byron Burns and Bill Bishop mostly - thank you both!), that basically explained why I was getting the issue: the .inp data from Daikin isn't importing correctly.
I just wanted to say that we're in July now, and this still hasn't been fixed (I downloaded the curve from Daikin a few days ago), so if you're having the problem, the fix proposed by Byron and Bill still works. It consists in to replacing the VRV Heating Curve with:
"VRV Heating EIR-F-EWB/ODB AC" = CURVE-FIT
TYPE = BI-QUADRATIC-T
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( -1.85025, 0.0620141, -0.000312822, 0.07145853,
-0.0003626328, -0.0007776424 )
| 4 | No.4 Revision |
@crdugin @crduggin just refreshed my memory. As of July 2014, there was still a mistake in Daikin's curves: eQuest has a limit of 80 characters per line... If you put more it gets truncated.
| 5 | No.5 Revision |
Here's a message message I wrote in July 2014 to the eQuest user mailing list: